Today I was up to ACV load testing by the use my Oscilloscope along of differential voltage probe and AC/DC current probe.
I did connect everything, but at the oscilloscope screen voltage phase and current phase, these was looking as reversed.
I did double check Oscilloscope settings, everything seemed correct and I was scratching my head for some time.
Current probe this has an arrow mark at the Jaws, therefore I did that connection correctly.
But I was using RED and Black test leads and banana plugs, and the differential volts probe this has also RED and Black banana plugs.
And this detail did not helped me to detect my error, fast enough.
Today's lesson learned: Make sure that both voltage and current probe, are both in synchronization with active phase (polarity check).
Or else you see everything with a not easy to explain phase error.
To make your life easier, confirm proper phase synchronization by the use of halogen lamps as load.