Three years later I have to add few corrections on this topic.
SUA1000XL this is designed to deliver at best
PF=0.8 , this was considered as
high-end at the year 2003~2004.
From the side of the AC load, it is a matter of product age and electronics in use, especially for Non-Linear loads, that is a switching power supply.
I do love to perform measurements, but especially at switching power supply, they are specific conditions so the test to be considered as valid.
The accuracy of the digital power meter, this is the last parameter so to be examined.
SUA1000XL this has 1000VA label and it is 800W.
An Computer PSU at the size of 750W, it should be stressed at 40% at least, for a proper Power factor evaluation.
In conclusion, if you are up to evaluate uninterruptible power supply Power Factor delivery, you should use a small
resistive load instead.
A pure resistive AC load due it nature will operate at PF=1.0, from the other hand any UPS inverter (on battery), this will deliver as max the supported Power Factor according the potentials of it own electronics.
Old in age or low cost, uninterruptible power supply they might deliver at their best
PF=0.6Now it starts to matter the quality of the AC power measuring device.
Low cost plug-in power meter (16A) , they are famous about not delivering Power Factor measurement with accuracy and at high in digits resolution.
So I have to declare my above testing as not a valid one, but I will leave this topic standing, as reminder of past made mistakes.
-------------------------------------------------------------------------
APC recommends UPS calibration this to be performed at not less than 40% of UPS Max loading capacity, what ever this be.
For the SUA1000XL this translates to 320W of load, and I did make my own load tester by combining 2 x 150W = 300W by the use classic style bulbs.
Then I did added and a third 40W of classic style bulb, and now I do perform UPS calibration with 340 Watts that is the recommended by the manufacturer.
Personally I will follow this recommendation, load testing at 40% or higher, and for power factor evaluation, when I am testing a UPS.